本课题是一宿舍楼的框架结构的设计,结构设计主要是取一榀框架,为三层、三跨,进行梁柱截面尺寸的估算,竖向荷载作用下及水平风荷载作用下的框架内力计算,梁柱的内力组合,配筋计算和桩基础计算。
框架内力计算方法为:恒载计算时采用弯矩二次分配法,活载计算时采用分层法逐层求得;计算风荷载时运用D值法计算。而后,根据《规范》进行内力组合,然后进行梁柱的截面校核及配筋计算。最后,楼板按弹性计算双向板配筋,桩基础进行承台的验算及配筋计算。
关键词 框架;结构设计;内力计算;内力组合;桩基础
This project is a dormitory design of a concrete frame construction. In the part of the frame calculation under vertical loads the frame is irregular which contain 3 layers and 3 span. Carried out to estimate the size of column section. The design of structure is made up of a frame calculation under vertical loads, the calculation of wind load under horizontal loads, the association of internal farces ,disposing steel bar for beams and column, two-way slab calculation, and pile foundation calculation.
The framework of the method of calculating internal forces: Dead load used in the calculation of secondary bending moment distribution method, Live load calculations obtained using layer-by-layer stratification; In horizontal wind load calculation used D value method. Then, According to "regulate" internal force to portfolio, Column and then proceed to check and reinforcement of the cross-section calculation. Finally, the floor plate by a flexible two-way,reinforcement calculated, Pile caps based on the calculation of check and reinforcement.
Keywords frames;structural design;calculating internal forces;the internal force combination;pile foundation
建筑面积:2252m2
建筑层数:3层
建筑高度:12.8m
某三层宿舍楼毕业设计计算书_secret.pdf
(1.08 MB, 下载次数: 7)